Abstract of Indian Electricity Rules:

1) Cut-out on consumer s premises:
The supplier shall provide a suitable cut-out in each conductor of every service-line other than an earthed or earthed neutral conductor or the earthed external conductor of a concentric cable within a consumer s premises, in an accessible position. Such cut-out shall be contained within an adequately enclosed fireproof receptacle.
Where more than one consumer is supplied through a common service-line, each such consumer shall be provided with an independent cut-out at the point of junction to the common service
Every electric supply line other than the earth or earthed neutral conductor of any system or the earthed external conductor of a concentric cable shall be protected by a suitable cut-out by its owner
No cut-out, page link or switch other than a linked switch arranged to operate simultaneously on the earthed or earthed neutral conductor and live conductors shall be inserted or remain inserted in any earthed or earthed neutral conductor of a two wire-system or in any earthed or earthed neutral conductor of a multi-wire system or in any conductor connected thereto with the following exceptionsSada) A page link for testing purposes, or (b) A switch for use in controlling a generator or transformer.

2) Danger Notices:
The owner of every medium, high and extra-high voltage installation shall affix permanently in a conspicuous position a danger notice in Hindi or English and the local language of the district, with a sign of skull and Bones on
(a) Every motor, generator, transformer and other electrical plant and equipment together with apparatus used for controlling or regulating the same;
(b) All supports of high and extra-high voltage overhead lines which can be easily climb-upon without the aid of ladder or special appliances.

3) Cables :
Flexible cables shall not be used for portable or transportable motors, generators, transformer rectifiers, electric drills, electric sprayers, welding sets or any other portable or transportable apparatus unless they are heavily insulated and adequately protected from mechanical injury.
Where the protection is by means of metallic covering, the covering shall be in metallic connection with the frame of any such apparatus and earth.
The cables shall be three core type and four-core type for portable and transportable apparatus working on single phase and three phases supply respectively and the wire meant to be used for ground connection shall be easily Identifiable
Where A.C. and D.C. circuits are installed on the same support they shall be so arranged and protected that they shall not come into contact with each other when live.

4) Safety:
Two or more gas masks shall be provided conspicuously and installed and maintained at accessible places in every generating station with capacity of 5 MW and above and enclosed sub-station with transformation capacity of 5 MVA and above for use in the event of fire or smoke.
Provide that where more than one generator with capacity of 5 MW and above is installed in a power station, each generator would be provided with at least two separate gas masks in accessible and conspicuous position.

5) High Voltage Equipments installations
High Voltage equipments shall have the IR value as stipulated in the relevant Indian Standard.
At a pressure of 1000 V applied between each live conductor and earth for a period of one minute the insulation resistance of HV installations shall be at least 1 Mega ohm Medium and Low Voltage Installations- At a pressure of 500 V applied between each live conductor and earth for a period of one minute, the insulation resistance of medium and low voltage installations shall be at least 1 Mega ohm

6) Every switchboard shall comply with the following provisions, namely:
A clear space of not less than 1 meter in width shall be provided in front of the switchboard;
If there are any attachments or bare connections at the back of the switchboard, the space (if any) behind the switchboard shall be either less than 20 centimeters or more than 75 centimeters in width, measured from the farthest outstanding part of any attachment or conductor;
If the space behind the switchboard exceeds 75 centimeters in width, there shall be a passage-way from either end of the switchboard clear to a height of 1.8 meters.

7) Declared voltage of supply to consumer:
In the case of low or medium voltage, by more than 6 per cent, or;
In the case of high voltage, by more than 6 per cent on the higher side or by more than 9 per cent on the lower side, or;
In the case of extra-high voltage, by more than 10 per cent on the higher side or by more than 12.5 per cent on the lower side.

8) Declared frequency of supply to consumer
Except with the written consent of the consumer or with the previous sanction of the State Government a supplier shall not permit the frequency of an alternating current supply to vary from the declared frequency by more than 3 per cent.

9) Meters, maximum demand indicators and other apparatus on consumer s premises
Any meter or maximum demand indicator or other apparatus placed upon a consumer s premises in accordance with section 26 shall be of appropriate capacity and shall be deemed to be correct if its limits of error are within the limits specified in the relevant Indian Standard Specification and where no such specification exists, the limits of error do not exceed 3 per cent above or below absolute accuracy at all loads in excess of one tenth of full load and up to full load Connection with earth Neutral conductor of a phase, 4 wire system and the middle conductor of a 2 phase, 3-wire system shall be earthed by not less than two separate and distinct connections with a minimum of two different earth electrodes of such large number as may be necessary to bring the earth resistance to a satisfactory value both at the generating station and at the sub-station. The earth electrodes so provided, may be interconnected to reduce earth resistance. It may also be earthed at one or more points along the distribution system or service line in addition to any connection with earth which may be at the consumer s premises
In the case of a system comprising electric supply lines having concentric cables, the external conductor of such cables shall be earthed by two separate and distinct connections with earth.The connection with earth may include a page link by means of which the connection may be temporarily interrupted for the purpose of testing or for locating a fault.All metal castings or metallic coverings containing or protecting any electric supply-line or apparatus shall be connected with earth and shall be so joined and connected across all junction boxes and other openings as to make good mechanical and electrical connection throughout their whole length.
Reply

#2
(01-16-2013, 05:40 PM)Guest Wrote: Dear Sir/Madam,

I request you to kindly send me copy of Indian Electricity Rules 2011 pdf.

Thanking you.
Reply

#3
Dear Sir/Madam,

I request you to kindly send me copy of Indian Electricity Rules 2011 pdf.

Thanking you.
Reply

#4
Dear Sir/ Madam,
Request you mail latest Indian Electricity Rules to [email protected]
Reply



Forum Jump:


Users browsing this thread:
1 Guest(s)

Powered By MyBB, © 2002-2024 iAndrew & Melroy van den Berg.